Re: batteries

Edwin Spector (espector@mltza.mlm.att.com)
Fri, 5 May 1995 14:24:02 -0700

>Gerry,

>one thing about batteries is that their discharge characteristics
>are not linear. If a battery is rated at 12 Amp-hour, it will
>actually provide this capacity at 1/20 or 1/10 of 12 A (depends
>on manufacturer). So you get (say) 12/20 = 0.6 A for 20 hours.

>Manufacturers refer to the A-h figure as the C-rating. The spec
>then applies for C/20 or C/10.

>If you double this current, you get _less_than_ half the discharge
>time.

>In general, high discharge rates (above C/20) will give a lower
>Amps x hours rating. Low discharge rates give a higher figure.

>Regarding charging, I looked up some figures for Panasonic sealed
>lead-acid batteries. For cyclic operation, (fairly full charge
>then discharge) they recommend two charging methods:

>Constant-Voltage: Use a supply of 14.6 to 15.0 V for a 12V battery.
>Initial current should be 0.4C or less. This is the quicker way.

>Constant-Current: Limit the charging current to 0.1C from a higher
>voltage source. Charging time control is recommended to prevent
>overcharge.

>Regards

>Edwin Spector
>edwin.spector@att.com